The Graphs in Fig 3A4-6. What does the vertical part of the characteristic mean?

There is a problem with these graphs. What is it and how should it be corrected?
Parents
  • gkenyon:
    AJJewsbury:

    they don't seem to be consistent with BS EN 60898 anyway - occasionally dangerously so

     


    Could you highlight where the inconsistencies are? Are you referring to Table 7?




    Back to this old discussion - https://communities.theiet.org/discussions/viewtopic/1037/24502 - which seemed to conclude that BS 7671 was claiming that certain rating of certain types of MCB would open within 5s for a given current whereas both BS EN 60898 and manufacturer's data suggested it could take up to 8s to disconnect.


      - Andy.


Reply
  • gkenyon:
    AJJewsbury:

    they don't seem to be consistent with BS EN 60898 anyway - occasionally dangerously so

     


    Could you highlight where the inconsistencies are? Are you referring to Table 7?




    Back to this old discussion - https://communities.theiet.org/discussions/viewtopic/1037/24502 - which seemed to conclude that BS 7671 was claiming that certain rating of certain types of MCB would open within 5s for a given current whereas both BS EN 60898 and manufacturer's data suggested it could take up to 8s to disconnect.


      - Andy.