A Good Design but............

Evenin' All,


I have been working in some holiday chalets today on a chalet park by the sea.


One chalet had a lovely new R.C.B.O. consumer unit in it. Beautifully installed. Very neat.


Another had a new split load consumer unit installed in it. Very nicely installed.


But why were they both a waste of money?


Z.

Parents
  • Andy has it I believe. All chalets have a site owned up front non time delayed R.C.D. So a single fault will knock out all of a chalet's electrics despite the owner's consumer unit being all R.C.B.O. or split load.


    Z.
Reply
  • Andy has it I believe. All chalets have a site owned up front non time delayed R.C.D. So a single fault will knock out all of a chalet's electrics despite the owner's consumer unit being all R.C.B.O. or split load.