jimmyhorns:
Any flaws so far?
Yes, if you plugged everything in and switched on, how much current would it add up to?
If you had only 2 ring finals in the house, you would subtract 12.8 A from the above, but the overall load would be the same.
32 A is a lot for a garage unless you have an EVCP. Could be 1 x 3 kW heater, but then what?
Try dividing your annual consumption by 365, then 24, and finally 0.23: that will give you your average load. It won't be much.
jimmyhorns:
Any flaws so far?
Yes, if you plugged everything in and switched on, how much current would it add up to?
If you had only 2 ring finals in the house, you would subtract 12.8 A from the above, but the overall load would be the same.
32 A is a lot for a garage unless you have an EVCP. Could be 1 x 3 kW heater, but then what?
Try dividing your annual consumption by 365, then 24, and finally 0.23: that will give you your average load. It won't be much.