Chris Pearson:jimmyhorns:
Any flaws so far?Yes, if you plugged everything in and switched on, how much current would it add up to?
32 A is a lot for a garage unless you have an EVCP. Could be 1 x 3 kW heater, but then what?
I thought that was the purpose of diversity - to correct for the fact that everything is unlikely to be on at the same time.
To answer your question, with everything plugged in and at full capacity, a lot of Amps, but in practice I cant see that happening.
For example, the immersion heater 'never' gets used etc.
In reality the cooker, washing machine, tumble dryer, hairdryer, full garage load and the lights are all that would be on simultaneously which would give:
21+13+8+32+2 = 76 Amps
The garage is more of a workshop and garage. 3kw heater + 4kw compressor + Mill + lathe + Plasma cutter + (insert any of the other toys here). Average demand is actually very low, but if its cold, the compressor kicks in while I am using the plasma cutter you are looking at 13 + 20 + 13 amps so already over spec - I'm careful with what runs simultaneously of course limiting it to one machine if the heater is running or two machines if it isnt.
Chris Pearson:jimmyhorns:
Any flaws so far?Yes, if you plugged everything in and switched on, how much current would it add up to?
32 A is a lot for a garage unless you have an EVCP. Could be 1 x 3 kW heater, but then what?
I thought that was the purpose of diversity - to correct for the fact that everything is unlikely to be on at the same time.
To answer your question, with everything plugged in and at full capacity, a lot of Amps, but in practice I cant see that happening.
For example, the immersion heater 'never' gets used etc.
In reality the cooker, washing machine, tumble dryer, hairdryer, full garage load and the lights are all that would be on simultaneously which would give:
21+13+8+32+2 = 76 Amps
The garage is more of a workshop and garage. 3kw heater + 4kw compressor + Mill + lathe + Plasma cutter + (insert any of the other toys here). Average demand is actually very low, but if its cold, the compressor kicks in while I am using the plasma cutter you are looking at 13 + 20 + 13 amps so already over spec - I'm careful with what runs simultaneously of course limiting it to one machine if the heater is running or two machines if it isnt.