Coding, basically!

Assume a scenario where everything else in a domestic property is satisfactory but with the following exceptions -

Consumer unit is plastic but not in an escape route.

Consumer unit is MK 16th ed split load, with single RCD protection on one side but with the mcbs replaced by RCBOs for all circuits on the other side.

No surge protection present, and all other devices function correctly.

Tails are 16mm but there a 60A fuse in the cut out - verified during a meter change recently.


So, what, if any coding should be applied? I am at a complete loss to fail it in any respect.

Parents
  • whj, why are you asking?


    SPD depends upon the situation. Even if a risk assessment shows that the installation is vulnerable, it is not mandatory, so I wouldn't code that.


    C3 for a non-compliant CU is all that I would give from the description.
Reply
  • whj, why are you asking?


    SPD depends upon the situation. Even if a risk assessment shows that the installation is vulnerable, it is not mandatory, so I wouldn't code that.


    C3 for a non-compliant CU is all that I would give from the description.