Coding, basically!

Assume a scenario where everything else in a domestic property is satisfactory but with the following exceptions -

Consumer unit is plastic but not in an escape route.

Consumer unit is MK 16th ed split load, with single RCD protection on one side but with the mcbs replaced by RCBOs for all circuits on the other side.

No surge protection present, and all other devices function correctly.

Tails are 16mm but there a 60A fuse in the cut out - verified during a meter change recently.


So, what, if any coding should be applied? I am at a complete loss to fail it in any respect.

Parents
  • Plastic consumer unit is a non-compliance so C3 for me. I am aware some documents mention escape routes which I dot agree with.


    The RCD protection complies with BS 7671 so no report.


    No SPD I would not mention unless overhead supply, building has LPS or safety services installed.


    16mm tails on a 60A fuse no issue.
Reply
  • Plastic consumer unit is a non-compliance so C3 for me. I am aware some documents mention escape routes which I dot agree with.


    The RCD protection complies with BS 7671 so no report.


    No SPD I would not mention unless overhead supply, building has LPS or safety services installed.


    16mm tails on a 60A fuse no issue.