broadgage:
I see little if any danger.
If the cable is into the chalet is rated for at least 50 amps, and is protected by a 50 amp MCB then the cable should be safe against thermal damage.
The cable does not "know" the difference between a short circuit current of say 300 amps on a high impedance supply, and a gross overload to 300 amps on a low impedance supply. In either case, the MCB should protect the cable against thermal damage.
Earth faults are more dangerous since a person could be exposed to about half line volts for a dangerous time whilst waiting for the MCB to trip. In this case that is handled by an RCD.
I would however consider this installation to be almost certainly unsatisfactory as regards voltage drop.
A short circuit current of 400 amps implies a 10% voltage drop at a load current of 40 amps, or 12.5% at the full load of 50 amps.
Volts from DNO could well be 220 volts actual.
Voltage at intake to chalet could be about 195 volts.
Voltage at point of use could be below 190 volts, almost certainly too low.
And this measurement was taken today with the chalet park closed so no loads were connected by other chalet users. I was concerned about the park when it is fully occupied.
Z.
broadgage:
I see little if any danger.
If the cable is into the chalet is rated for at least 50 amps, and is protected by a 50 amp MCB then the cable should be safe against thermal damage.
The cable does not "know" the difference between a short circuit current of say 300 amps on a high impedance supply, and a gross overload to 300 amps on a low impedance supply. In either case, the MCB should protect the cable against thermal damage.
Earth faults are more dangerous since a person could be exposed to about half line volts for a dangerous time whilst waiting for the MCB to trip. In this case that is handled by an RCD.
I would however consider this installation to be almost certainly unsatisfactory as regards voltage drop.
A short circuit current of 400 amps implies a 10% voltage drop at a load current of 40 amps, or 12.5% at the full load of 50 amps.
Volts from DNO could well be 220 volts actual.
Voltage at intake to chalet could be about 195 volts.
Voltage at point of use could be below 190 volts, almost certainly too low.
And this measurement was taken today with the chalet park closed so no loads were connected by other chalet users. I was concerned about the park when it is fully occupied.
Z.