mapj1:
Quite right, PSSC of 400A, assume supply voltage at origin of 240- effective Zs willl be no better than 240V/400A or about 0.6 ohms.
Now there is no time limit for disconnecting L-N faults, so those are OK, but to fire a B50 smartly on an earth fault could take as much as 250A, and if it is a C50 then 500A.
An RCD or RCBO removes these concerns, totally.
I'm with Broadgage, folk will notice the lights dim when the neighbours put the kettle on. If it is a real problem is less clear, appliances vary in how well they behave on low voltage.
It may be the transformer is private to the site and the taps are set a bit high to allow for this.
M.
Hello Mike,
there us no site transformer. The supply comes in from overheads. There are five overhead lines on poles. I will take a closer look when I get time. The main earthing terminal is connected by a black 25mm single cable coming up from the ground next to the main underground incoming main supply cable. I do not know its origin.
My next investigation will be of the 25mm2 twin underground S.W.A. cable supply to the most remote chalet. It comes from a distant distribution board and is protected by a C63 M.C.B. This is the cable with the P.S.C.C. of 400 Amps at its end. What will an earth fault produce if somebody drives a metal pole through it?
Note. E.F.L.I. at main intake room = sub 1.0 Ohm. P.S.C.C. = 1.68kA.
Z.
mapj1:
Quite right, PSSC of 400A, assume supply voltage at origin of 240- effective Zs willl be no better than 240V/400A or about 0.6 ohms.
Now there is no time limit for disconnecting L-N faults, so those are OK, but to fire a B50 smartly on an earth fault could take as much as 250A, and if it is a C50 then 500A.
An RCD or RCBO removes these concerns, totally.
I'm with Broadgage, folk will notice the lights dim when the neighbours put the kettle on. If it is a real problem is less clear, appliances vary in how well they behave on low voltage.
It may be the transformer is private to the site and the taps are set a bit high to allow for this.
M.
Hello Mike,
there us no site transformer. The supply comes in from overheads. There are five overhead lines on poles. I will take a closer look when I get time. The main earthing terminal is connected by a black 25mm single cable coming up from the ground next to the main underground incoming main supply cable. I do not know its origin.
My next investigation will be of the 25mm2 twin underground S.W.A. cable supply to the most remote chalet. It comes from a distant distribution board and is protected by a C63 M.C.B. This is the cable with the P.S.C.C. of 400 Amps at its end. What will an earth fault produce if somebody drives a metal pole through it?
Note. E.F.L.I. at main intake room = sub 1.0 Ohm. P.S.C.C. = 1.68kA.
Z.