Minimum and Maximum Prospective Fault current calculations

Former Community Member
Former Community Member
hello

I am studying IET Electrical Installation and Design Guide 4th edition. and I am confused about using Cmin and Cmax to calculate Ipf and Ief. When do we use Cmin and Cmax to calculate the Minimum Prospective fault current (Ief) ??
Parents
  • Cmax is used in BS 7671 to determine Im and RA ev in section 722, from Amendment 1:2020.

    Ah, good spot - I'd not noticed that one!

     
    BUT I could argue that  Cmax should be used to calculate I where adiabatic is used (S being proportional to I).

    Humm, but not just proportional to I - there a t in there too and t tends to vary with I. For MCBs I'd agree that t doesn't reduce much as I increases so using Cmax is likely to give the worst case, but for fuses t tends to decrease quite rapidly as I increases - so often the worst case energy let-through is for lower fault currents - so perhaps in some cases Cmin would be the defensive choice.


      - Andy.
Reply
  • Cmax is used in BS 7671 to determine Im and RA ev in section 722, from Amendment 1:2020.

    Ah, good spot - I'd not noticed that one!

     
    BUT I could argue that  Cmax should be used to calculate I where adiabatic is used (S being proportional to I).

    Humm, but not just proportional to I - there a t in there too and t tends to vary with I. For MCBs I'd agree that t doesn't reduce much as I increases so using Cmax is likely to give the worst case, but for fuses t tends to decrease quite rapidly as I increases - so often the worst case energy let-through is for lower fault currents - so perhaps in some cases Cmin would be the defensive choice.


      - Andy.