CSA of main earthing conductor for TT

Morning! Has the minimum CSA of the main earth to the rod changed in the 18th ed? I can't find any reference to it in the BBB (except when buried). 

I have a guy who is insisting on 16mm whereas I "thought" it could be much less if not buried and protected against corrosion and mechanical damage. I only have table 4.4(ii) in my 17th ed OSG as corroboration. Thanks.
Parents
  • davezawadi (David Stone):

    I gave the reg number Z. 2.5 with mechanical protection is permitted. 543.1.1, at least in my book, why are you saying 4mm? Grumpy, Andy and I seem to prefer (option) to use 10mm anyway. Not that it matters.


    Hello Dave,

                        all contractors around here use 16mm2 for earth rods at TT installations. I suppose that it is readily available, off the van, and it has strength against bashing and chemical attack. Considering its important safety role I use it as well. I have never seen 4.0mm2 or 2.5mm2 used to an earth rod ever. I did once use 10mm2 though. Considering that the run is normally a shortish one its cost is not too great.


    So, according to 543.1.1 we can size a protective conductor by calculation (see 543.1.3)


    or


    Select it from table 54.7 (see 543.1.4).


    Further the reg. says that if the protective conductor is


    (iii) not an integral part of a cable.


    OR


    (iv) not formed of conduit, ducting or trunking,


    OR


    (v) not contained in an enclosure formed by a wiring system.


    then the cross sectional area shall not be less than 2.5mm2 copper equivalent if protected against mechanical damage, or 4.0mm2 copper equivalent if mechanical protection is not provided.


    Most earth rods have the top exposed in the garden, along with the cable, so to my mind that requires at least 4.0mm2 as it is not protected against bashing. If we bury the cable in an earth pit that is extra work and expense. It also has to be at least 16mm2 copper in size if buried. (Table 54.1).


    Z.






     


Reply
  • davezawadi (David Stone):

    I gave the reg number Z. 2.5 with mechanical protection is permitted. 543.1.1, at least in my book, why are you saying 4mm? Grumpy, Andy and I seem to prefer (option) to use 10mm anyway. Not that it matters.


    Hello Dave,

                        all contractors around here use 16mm2 for earth rods at TT installations. I suppose that it is readily available, off the van, and it has strength against bashing and chemical attack. Considering its important safety role I use it as well. I have never seen 4.0mm2 or 2.5mm2 used to an earth rod ever. I did once use 10mm2 though. Considering that the run is normally a shortish one its cost is not too great.


    So, according to 543.1.1 we can size a protective conductor by calculation (see 543.1.3)


    or


    Select it from table 54.7 (see 543.1.4).


    Further the reg. says that if the protective conductor is


    (iii) not an integral part of a cable.


    OR


    (iv) not formed of conduit, ducting or trunking,


    OR


    (v) not contained in an enclosure formed by a wiring system.


    then the cross sectional area shall not be less than 2.5mm2 copper equivalent if protected against mechanical damage, or 4.0mm2 copper equivalent if mechanical protection is not provided.


    Most earth rods have the top exposed in the garden, along with the cable, so to my mind that requires at least 4.0mm2 as it is not protected against bashing. If we bury the cable in an earth pit that is extra work and expense. It also has to be at least 16mm2 copper in size if buried. (Table 54.1).


    Z.






     