CSA of main earthing conductor for TT

Morning! Has the minimum CSA of the main earth to the rod changed in the 18th ed? I can't find any reference to it in the BBB (except when buried). 

I have a guy who is insisting on 16mm whereas I "thought" it could be much less if not buried and protected against corrosion and mechanical damage. I only have table 4.4(ii) in my 17th ed OSG as corroboration. Thanks.
Parents
  • Yep.


    Both 542.3.1 and 543.1.1 says 2.5 mm in the absolute minimum size.
Reply
  • Yep.


    Both 542.3.1 and 543.1.1 says 2.5 mm in the absolute minimum size.