4mm2 twin and earth cable

Former Community Member
Former Community Member
regarding 4mm2 cable was it ever available in the old colours with solid conductors rather than the 7 strands version? Ive just done a pre - inspection of a property before doing an EICR and found 2 radial circuits fed from 32A MCBS. The cables appear to be  larger than 2,5mm2 . I'm going back to inspect this property with a view to reducing the MCB's to 20A if if they are 2.5mm2. I'm also taking  a Vernier  gauge to measure the cable diameters and compare to reference tables.

The installation is approximately 30 years old but is in very good condition.
Parents
  • Normcall:

    Don't forget 7/029 is nearly equal to 3mm


    I think that the concern was with a solid conductor cable Norm.


    Z.


Reply
  • Normcall:

    Don't forget 7/029 is nearly equal to 3mm


    I think that the concern was with a solid conductor cable Norm.


    Z.