This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

4mm2 twin and earth cable

Former Community Member
Former Community Member
regarding 4mm2 cable was it ever available in the old colours with solid conductors rather than the 7 strands version? Ive just done a pre - inspection of a property before doing an EICR and found 2 radial circuits fed from 32A MCBS. The cables appear to be  larger than 2,5mm2 . I'm going back to inspect this property with a view to reducing the MCB's to 20A if if they are 2.5mm2. I'm also taking  a Vernier  gauge to measure the cable diameters and compare to reference tables.

The installation is approximately 30 years old but is in very good condition.
Parents
  • a 20 amp cartridge/mcb backs up 20 amp cables.

    Unless of course you consider the famous ring circuit...


     
    Aluminium started at 16mmsq.

    On the DNO side perhaps, but plain aluminium was certainly available in common T&E sizes before the wiring regs prohibited the smaller sizes - e.g. (pinched from another forum):
    c7c48becdf5b0711aa59d0cc39bf27e3-original-altande.jpg


      - Andy.
Reply
  • a 20 amp cartridge/mcb backs up 20 amp cables.

    Unless of course you consider the famous ring circuit...


     
    Aluminium started at 16mmsq.

    On the DNO side perhaps, but plain aluminium was certainly available in common T&E sizes before the wiring regs prohibited the smaller sizes - e.g. (pinched from another forum):
    c7c48becdf5b0711aa59d0cc39bf27e3-original-altande.jpg


      - Andy.
Children
No Data