Cable current rating advice
Hi all, I would like to verify something with respect to current carrying capacity of cable. Specifically vehicle single core DC circuits.
Looking at 16mm wire not worrying about voltage drop. manufacturers are ratting this at 110A and on a forum I subscribe to people have been advised 125A is ok.
The cable is rated at 70 deg as shown on the suppliers site linked below.
16mm supplier
Am I wright that this comes under
Table 4D1A
Single-core 70°C Thermoplastic Insulated Cables, Non-Armoured, with or without Sheath
Reference Method C (clipped direct) This will be between battery to battery not in any conduit or insulation
So is rated as 87A
I would be interested in your advice as it has been several years since I used these tables
  • In this particular case, the proposed 16mm cable is PROBABLY fine, but "probably" makes me a little nervous and I would be inclined to upsize to 25mm and sleep soundly.
    There are so many unknows in vehicle electrics, that I consider "one size up" to be sensible.
    The EXACT current may be unknown, is the given figure an absolute maximum ? or is it a nominal figure that might be exceeded by say 10% ?
    Ambient temperature is even more unknown than with a building, future use in the tropics with electric air conditioning ?
    Other heat sources near the cables ? engine coolant system, central heating equipment ?
    Just go up a size, the expense is trivial for a short length in a presumably valuable vehicle.
    Thank you both for some very useful information. The design will actually be 40 amp fused but I wanted to know more about cable rating for vehicle cabling which you have both provided. On a different forum a guy was running 16mm with 80 amp fuse protection which from our conversation here is not good. Especially when they are only using 30 amps load.
  • I'm guessing this is a auxiliary (leisure) battery connection in the motorhome - if so the requirements for fault protection mean you can't just use plain unsheathed cables for battery connections - they need to be sheathed (or over taped) as far as the first overcurrent protective device (fuse) (BS 7671 reg A721.55.3.6 or similar wording in BS EN 1648)  - which might derate them a little from the manufacturer's rating for unsheathed use. (Unfortunately the automotive-style battery terminal mounted fuses aren't acceptable way to avoid that as overcurrent protective devices aren't allowed in the auxiliary battery compartment).
    Yes you are correct this is a charging circuit. Not fully understanding your post, are you saying all charging wiring needs to be twin sheathed. From the van we have the dealer has used single core cabling for teh charging circuit, this was also the same on the past three vans we have owned all from different dealers.
    Also our battery in the leisure area is under he passenger seat and already has protection device fitted in this area. For the vehicle battery this is under the passenger foot well and has fuses directly attached to the batter. Are you saying you cannot have any protection (fuses or circuit breakers) under the passenger seat. This van does not really have a battery compartment for leisure battery as it is open space under the seat as all van builds are.
  • Well  it is quite possible that the installation is neither to BS7671 nor EN 1648, it is quite likely just to auto electrician car standard. You could thread some flexi conduit over the battery leads to achieve a similar effect.
    M.
  • steve14:
    Not twin-core sheathed - as you'd have to removed the sheath before you got to the battery terminals and what you're trying to achieve is something akin to double/reinforced insulation between the two poles or anything they're connected to either of them (e.g. the chassis). When I re-did our caravan I just used a couple of lengths of heat-shrink sleeving individually over the single core battery cables - although it seems that just wrapping with tape is also considered sufficient.
    As I see it, automotive fuses are at best semi-enclosed - at at their moment of operation will generate temperatures that will melt metal and likely produce an arc as well. Really not the best thing to have next to a rather temperature sensitive battery that can under certain conditions evolve flammable and potentiall explosive hydrogen gas (at least in the case of the various forms of lead-acid battery). The risks might well be tolerable in an engine compartment where you'd typically have good ventilation and a steel bulkhead between the battery and passenger compartments but perhaps the same approach isn't quite so comfortable inside a passenger compartment - especially one often used for sleeping.
    I know what you mean about there often not being an obvious battery compartment especially in older vans (newer ones tend to have a battery box accessible from outside) - although (at least with lead-acid) batteries there's usually at least a plastic container with a loose fitting lid - to contain any escaped electrolyte - personally I'd like to see the battery fuse at least comfortably outside of that - but it's probably a bit of engineering judgement based on how close and how well ventilated.
    I'd also beleive that that caravan industry doesn't seem very good at adhering to its own standards - our (second hand) van came with an apparently professionally fitted motor mover - where the installer seemed to think it adquate not only to use cables at least one size smaller than the manufacturer recommended (and the insulation was showing signs of discolouration and cracking by the time we got it) but to leave the entire system completely unfused - so nothing but a relay between a 100Ah leisure battery and thinwall singles tie-wrapped to the underside of the chassis (alongside the gas pipework of course),
    As I understand it, (BS) EN 1648 (Leisure accommodation vehicles. 12 V direct current extra low voltage electrical installations) is the standard that should be followed (part 1 for caravans or part 2 for motor caravans) and BS 7671 section A721 seems to be lightly edited copy of the same. It's the BS 7671 version I'm most familiar with and it is possible that some details are different BS EN 1648. A lot of it does seem to have been written with lead-acid battery technology in mind, so it might be that some of the precautions aren't necessary with other battery chemistries - but others here will have a better idea of that than me.
    This is a new van. Fiat ducato. The engine battery is under the passenger foot well same as most vans and the fuses are attached to the battery.
    the leisure battery is not in a seal box but under the passenger seat. It is a lead acid battery but a sealed one. No chance electrolyte spillage. They are designed to be installed like this. I will be changing this to lithium soon again sealed battery.
  • steve14:
    The starter battery would be part of the basic vehicle so won't come under BS EN 1648 but under some automotive standard - which likely allows fuses next to the battery (and I might suspect is nominally outside of the passenger compartment and possibly ventilated to the outside, even if it's accessible from the passenger area). The leisure battery would come under BS EN 1648 - and I suspect even "sealed" lead acid types are usually valve regulated - i.e. can still emit hydrogen etc. under some fault conditions - so if in a passenger area it seems sensible to me to keep fuses etc a little away from the battery.