Volt drop at the intake - Just looking to compare with sunny Thailand.

A nice easy one.


On a "standard" UK domestic supply what sort of volt drop would you expect at the intake for a load of 50A?


In an urban environment and in a rural environment.


We are dropping about 30V (from a nominal 220V) at 50A, of course the other loads in the village may already have pulled things down to 205V!!

Parents
  • for an 800m run it may be worth considering a pair of transformers one at each end an hopping up to 690 or some other voltage depending what your local regs permit.

    there will be standing losses, but unless you really use no current, then it becomes worth considering after a few hundred metres.

    M.
Reply
  • for an 800m run it may be worth considering a pair of transformers one at each end an hopping up to 690 or some other voltage depending what your local regs permit.

    there will be standing losses, but unless you really use no current, then it becomes worth considering after a few hundred metres.

    M.