Sparkingchip:
The Onsite Guide puts it much more succinctly:
7.2.2 Socket-outlet circuits
As a rule of thumb for rings, unfused spur lengths should not exceed 1/8 the cable length from the spur to the furthest point of the ring.
So if the spur is adjacent to the DB, that gives 80 m to the furthest point and 160 m all the way round. That's a long ring!
In fact all may be well if the load is not great. Perhaps an FCU in the spur would help?
ETA: IMHO spurs should be avoided. We are not aiming to make a coronavirus! ?