BUT it sounds like no RCD at the origin, so be aware it is not ideal, you need some sort of RCD covering the socket and in the current regs to rely on an RCD socket to do this is strictly a non-compliance.
Mike
This needs expanding, the issues of having RCD sockets rather than RCD protection at the consumer unit:
MrJack96:
So are you saying running an swa outside to feed an rcd socket isn’t compliant?
Yes. Odd though it may seem, they are not a type of RCD that is approved in BS 7671. However, I certainly haven't rushed to change my 15th Edn installation at home. I have simply replaced defective SRCDs with new ones.
If you search through the Forum, you will find quite a bit of discussion on the topic.
MrJack96:
Well there’s the next problem it’s fed from a Wylex fuse board with plug in type fuses. ??
Let's get something clear. BS 7671 is not retrospective. If the owner doesn't want to replace the DB, but is happy to pay for an SRCD, that is the safest option. Go with it!