NICEIC consumer unit labels

Former Community Member
Former Community Member
Hi


I am looking to add some labels similar to the NICEC one bellow prior to my Napit assessment and I am unsure what value is expected in the box for maximum disconnect time.

Does any one know if it should be Circuit breaker disconnect time, *1 or *5 time for the RCD?


Also for the box for type of wiring I assume they are looking for T+E, SGL, SWA etc.


Thanks


Alan


e10908bbd9a85a18e8332f923bd71c16-huge-image.png

Parents
  • Normally I'd expect to see  0,4 sec (TNx), or 0.2 sec (TT) for finals or 5 seconds(TNx) or 1sec (TT) for large submains and really mean longest ADS time

    permitted by the regs. as the max limit.


    The test results however should always be shorter ? or we have the wrong sort of RCD fitted, or something is broken.

    description


    1mm T&E or 25mm SWA or what ever. If mixed, the smaller. so a mix of 1,5 and 1,0 t and E would be treated as if all 1mm if there is not room on form for both.

    M.


Reply
  • Normally I'd expect to see  0,4 sec (TNx), or 0.2 sec (TT) for finals or 5 seconds(TNx) or 1sec (TT) for large submains and really mean longest ADS time

    permitted by the regs. as the max limit.


    The test results however should always be shorter ? or we have the wrong sort of RCD fitted, or something is broken.

    description


    1mm T&E or 25mm SWA or what ever. If mixed, the smaller. so a mix of 1,5 and 1,0 t and E would be treated as if all 1mm if there is not room on form for both.

    M.