Sizing of flylead to SWA

Sorry about idiot-level question. 

3 no Distribution circuits, 3 phase, one each in 4 x 16, 4 x 25 and 4 x 35mm XLPE/SWA and each with separate 16mm cpc alongside.  The armour will of course be in parallel with the external cpc but ignored for sake of R1+R2 etc. however doing belt-and-braces by using Earthing Nuts at both ends.  Other than treating the armour as extraneous part to be supplementary bonded, in which case presumably the 4mm (544.2.1) rule applies, is there any proper guidance on the size of the fly lead to these Earthing Nuts?  Cable sizes quoted above are required primarily from voltage drop considerations.

These circuits are taken from a larger distribution circuit, overall on TN-C-S with additional earth rod at the end of the primary Distrib cct, which is in the middle of a field.  There are no other parts or services that require Supplementary Bonding.

Thanks for your advice.
Parents
  • Thanks for giving that elusive (to me anyway) bit of clarity.

    Correct presumption Mike, load ends are in camping cabins / feeder cabinet.  I'll go for 16mm to match the external cpc - well within MCB rating.

    This is actually voluntary work for a youthwork charity in my retirement, so no van and no spare cash.

    G.
Reply
  • Thanks for giving that elusive (to me anyway) bit of clarity.

    Correct presumption Mike, load ends are in camping cabins / feeder cabinet.  I'll go for 16mm to match the external cpc - well within MCB rating.

    This is actually voluntary work for a youthwork charity in my retirement, so no van and no spare cash.

    G.