John Peckham:
D4G
You have to notify the ENA if your MD will go over 50A and they will notify the DNO.
The best way to verify your MD is not by calculation but power logging the supply over a week. either using a power logger or a recording clamp meter that will last a week on the battery and will not automaticay turn off after a set period.
Having established your MD add the EV demand and you have your new MD. With a 60A main fuse you are going to need load curtailment or s supply upgrade.
60a is the figure, if below 60 then you can notify DNO after installation but if above 60 then you should notify before installation.
Logging the consumption is the answer but not so practical and I doubt a common practice being as customers want answers today!
I believe the norm is to request a 100a upgrade before EVSE installation, this is what I asked for when was presented with the ENA form.
John Peckham:
D4G
You have to notify the ENA if your MD will go over 50A and they will notify the DNO.
The best way to verify your MD is not by calculation but power logging the supply over a week. either using a power logger or a recording clamp meter that will last a week on the battery and will not automaticay turn off after a set period.
Having established your MD add the EV demand and you have your new MD. With a 60A main fuse you are going to need load curtailment or s supply upgrade.
60a is the figure, if below 60 then you can notify DNO after installation but if above 60 then you should notify before installation.
Logging the consumption is the answer but not so practical and I doubt a common practice being as customers want answers today!
I believe the norm is to request a 100a upgrade before EVSE installation, this is what I asked for when was presented with the ENA form.