perspicacious:
I agree, the black ones are only rated at 80 A by the DNO so if you ask for 81 A, it will trigger the need to change it to the newer DMC type that are rated at 100 A by the DNO. This in turn will trigger network involvement and possibly reinforcement at consumer's cost as the standard supply is typically 15 kVA for domestic.
Regards
BOD
It all started as I was taught to ask for upgrade to 100A if installing EVSE. This would just involve upgrading meter tails to 25mm. This by the way has been done already and a smart meter fitted. I’m guessing if the cut out has been upgraded it would have been appropriately labelled...
perspicacious:
I agree, the black ones are only rated at 80 A by the DNO so if you ask for 81 A, it will trigger the need to change it to the newer DMC type that are rated at 100 A by the DNO. This in turn will trigger network involvement and possibly reinforcement at consumer's cost as the standard supply is typically 15 kVA for domestic.
Regards
BOD
It all started as I was taught to ask for upgrade to 100A if installing EVSE. This would just involve upgrading meter tails to 25mm. This by the way has been done already and a smart meter fitted. I’m guessing if the cut out has been upgraded it would have been appropriately labelled...