The maximum demand situation is an absolute mess at the moment. I adopt the view taken by Jon Steward. My nett increase is zero as I only use EVSE with load curtailment. I make my assessment of each situation based on the ENA cut out guidance and whether there are any combustible items stored within the immediate area. If I feel a safe install can proceed, I install and notify the DNO afterwards. I make it abundantly clear to the customer that the DNO may require upgrade not because of the additional EVSE but because their MD was theoretically already in excess of the supply capacity.
I have been asked on occasion by the DNO (NIE) to advise if the load curtailment is fail safe, ie. that the charge current will be switched off in the event of any failure of the load monitoring circuit. I use the Myenergi Zappi for domestic installs so I simply sent the DNO their answer to that. I have had no response and that was at least 6months ago.
We all must make sure our installations are safe but the burden of supply capacity has to be borne by the DNOs who can in turn deal directly with any agitation from their customers!
The 60A load limit as to whether the DNO is informened before or after is a nuisance, surely the majority of houses have a MD of more than 28A (32A to be added for the EVSE)??
I will be pushing the Zappi as my prefered unit due to all the safety features being included although more maufacturers are going this way now.
lyledunn:
The maximum demand situation is an absolute mess at the moment. I adopt the view taken by Jon Steward. My nett increase is zero as I only use EVSE with load curtailment. I make my assessment of each situation based on the ENA cut out guidance and whether there are any combustible items stored within the immediate area. If I feel a safe install can proceed, I install and notify the DNO afterwards. I make it abundantly clear to the customer that the DNO may require upgrade not because of the additional EVSE but because their MD was theoretically already in excess of the supply capacity.
I have been asked on occasion by the DNO (NIE) to advise if the load curtailment is fail safe, ie. that the charge current will be switched off in the event of any failure of the load monitoring circuit. I use the Myenergi Zappi for domestic installs so I simply sent the DNO their answer to that. I have had no response and that was at least 6months ago.
We all must make sure our installations are safe but the burden of supply capacity has to be borne by the DNOs who can in turn deal directly with any agitation from their customers!
The 60A load limit as to whether the DNO is informened before or after is a nuisance, surely the majority of houses have a MD of more than 28A (32A to be added for the EVSE)??
I will be pushing the Zappi as my prefered unit due to all the safety features being included although more maufacturers are going this way now.