This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Earthing of VSAT dishes

Former Community Member
Former Community Member
I am trying to apply the principles of BS 7671 to VSAT installations in Africa. My chief concern is the connection of the VSAT dish to the electrical supply provided by the customer. The standard practice I've adopted is shown in the attached sketch. The metallic parts of the dish are connected with copper conductors and then to an earth spike (or spikes) near the dish foundations. The earth cable is then run (either in a conduit of buried) to the equipment building. At the entry to the building, the earth cable is used by surge arrestors fitted to the RF cables. The earth cable then runs to an earth bar fitted into the equipment cabinet.  The mains supply to the equipment is supplied by the customer, the earth of which is also connected to the cabinet's earth bar. The power supplied by the customer may be from a generator 100% of the time, or more like comes from the town's municipal supply, These supplies are often erratic so a back-up generator is often in use, and as a matter of course we always fit an on-line UPS. Is this approach sensible?  Thanks for any assistance.59494298b3459314364a34dca9abf95a-huge-vsat-earthing.jpg
Parents
  • Brian


    That is a similar arrangement adopted here in the UK for mobile phone masts. A lightning protection (LPS)  rod at the highest point on the mast with the mast connected to earth electrodes at the base. The signal co-ax cables have  inline surge protection before they enter the equipment cabin. All the mains supply to the equipment racks has Type 1 and Type 2 surge protection with any metallic parts of the cabin, external mains feed pillars, any metallic fence all connected to auxillary electrodes all connected together with tape and to the LPS earthing.


    I am no expert but I think it would be better to have your surge arrestor on the earth outside the building rather than inside. Also I am not over keen in the long runs of earth from your surge arrestor to the earth electrode. I would be much happier to see another electrode directly connected to your surge arrestor outside the building. In the UK BS 7671 requires the total length of the connection of a live conductor to a Surge Protection Device and the earth connection ideally should not exceed 0.5m and  not to exceed 1m. Dumping any transient to earth outside the building would be my preference.
Reply
  • Brian


    That is a similar arrangement adopted here in the UK for mobile phone masts. A lightning protection (LPS)  rod at the highest point on the mast with the mast connected to earth electrodes at the base. The signal co-ax cables have  inline surge protection before they enter the equipment cabin. All the mains supply to the equipment racks has Type 1 and Type 2 surge protection with any metallic parts of the cabin, external mains feed pillars, any metallic fence all connected to auxillary electrodes all connected together with tape and to the LPS earthing.


    I am no expert but I think it would be better to have your surge arrestor on the earth outside the building rather than inside. Also I am not over keen in the long runs of earth from your surge arrestor to the earth electrode. I would be much happier to see another electrode directly connected to your surge arrestor outside the building. In the UK BS 7671 requires the total length of the connection of a live conductor to a Surge Protection Device and the earth connection ideally should not exceed 0.5m and  not to exceed 1m. Dumping any transient to earth outside the building would be my preference.
Children
No Data