How can you determine by measurement if you have two separate sources if supply?

Former Community Member
Former Community Member
Hi everyone, I am looking for some answers for the following situation:


There are two identical three phase step-down transformers 11kV to 0.4kV, connected to a 11kV ring main, each have an UPS system connected downstream and both are connected to the same Automatic Transfer Switch:

TX1 → UPS1 → ATS SOURCE 1

TX2 → UPS2 → ATS SOURCE 2


I want to plug in a parallel supply ciruit in the ATS for source 1 (considering the new and existing circuit would be live) and I want to double check by measurement that the new circuit is not connected to another source by mistake.


I have measured at the ATS the voltage and frequency on the same source, U=400V / Uo=230V / 50Hz and I wasn't expecting any voltage between the two separate sources but this is what i found:

TX1/ L1 - TX2/ L1 = 2V / 700-800Hz

TX1/ L1 - TX2/ L2 = 400V / 50Hz

TX1/ L1 - TX2/ L3 = 400V / 50Hz


TX1/ L2 - TX2/ L1 = 400V / 50Hz

TX1/ L2 - TX2/ L2 = 2V / 700-800Hz

TX1/ L2 - TX2/ L3 = 400V / 50Hz


TX1/ L3 - TX2/ L1 = 400V / 50Hz

TX1/ L3 - TX2/ L2 = 400V / 50Hz

TX1/ L3 - TX2/ L3 = 2V / 700-800Hz


From the readings above I can see that the different frequency between TX1/ L1 and TX2/ L1 etc is an indicator of a different source of supply.


Is my assumption correct? 

Why is there a voltage between the two sources of supply if there is no physical connection due to the internal windings in the transformer?

Why is there a highly fluctuating frequency between the same lines of the two sources?


Thank you in advance!


Andrei Ionescu
Parents
  • Of course you will get a potential difference between the two sources as the neutrals will be linked which, by the way, must be kept intact with UPS systems to prevent floating neutrals - 3 pole switching only.

    The 700-800Hz seems like the PCM frequency of the UPS invertors and is being imposed on the line albeit at a very low level, I think that is quite normal.

    Not sure about the rationale of paralleling another source alongside the existing source to one leg of the ATS, sounds a bit dodgy to me.
Reply
  • Of course you will get a potential difference between the two sources as the neutrals will be linked which, by the way, must be kept intact with UPS systems to prevent floating neutrals - 3 pole switching only.

    The 700-800Hz seems like the PCM frequency of the UPS invertors and is being imposed on the line albeit at a very low level, I think that is quite normal.

    Not sure about the rationale of paralleling another source alongside the existing source to one leg of the ATS, sounds a bit dodgy to me.