broadgage:
Larger or more complex substations and switchrooms that I have seen DO have emergency lighting. Provision of same greatly simplifies fault finding, alterations and repairs, and facilitates escape if it all goes horribly wrong.
I fail to see that properly installed emergency lighting would be a fire risk. Standard self contained battery operated emergency lights are often the cheapest and easiest to install. A better quality solution IMHO is a small central battery system but with the output switched by the same control as the room lighting. This avoids the needless discharging of the battery during a prolonged external power failure.
Larger substations often have significant battery capacity anyway (for the protection relays, recharge motor mechs, SCADA etc) - emergency lighting is often supplied via these batteries as it presents a fairly small proportion of the standing load on the batteries
Regards
OMS
Switching emergency lighting from the normal lighting switch is quite tricky but I once did it by having the normal lighting switch close to energise a N/C relay that turned the lights off, one pole for normal, one pole for the emergency lights. This meant that when the switch opened or when the normal supply failed, the relay would close and the emergency lights came on.