Good morning

I have a big student accomodation building with a dedicated DNO substation and a nearby LV switchroom where the DNO will place the cut-out ACB (1250A)

On the opposite wall we are putting our Main Distribution Panel.

Now, usually in previous cases the DNO cut out and the MDP panel are side by side and the tails go into a trunking.

In this case they will go on a ladder. From the DNO cut out box up to the ceiling, across the room and down to the MDP panel.

I know that ladder does not offer mechanical protection.

Can I still go with tails on the ladder? Or I need XLPE/SWA single cores in this case?

Is there something in BS7671 that prohibits the use of double insulated tails on a ladder?


Sorry for my ignorance

Kind Regards
Parents
  • I have only seen a DNO MCCB cut out in the consumers premises in the form of a steel cabinet which is locked on and the consumer does not have access.


    In UKPN land you present the tails to them and they terminate in to their equipment usually in the sub station and they will not accept finely stranded HO7RNF type cables.



    Just use AWAs and everyone will be happy.
Reply
  • I have only seen a DNO MCCB cut out in the consumers premises in the form of a steel cabinet which is locked on and the consumer does not have access.


    In UKPN land you present the tails to them and they terminate in to their equipment usually in the sub station and they will not accept finely stranded HO7RNF type cables.



    Just use AWAs and everyone will be happy.