DNO Tails on ladder

Good morning

I have a big student accomodation building with a dedicated DNO substation and a nearby LV switchroom where the DNO will place the cut-out ACB (1250A)

On the opposite wall we are putting our Main Distribution Panel.

Now, usually in previous cases the DNO cut out and the MDP panel are side by side and the tails go into a trunking.

In this case they will go on a ladder. From the DNO cut out box up to the ceiling, across the room and down to the MDP panel.

I know that ladder does not offer mechanical protection.

Can I still go with tails on the ladder? Or I need XLPE/SWA single cores in this case?

Is there something in BS7671 that prohibits the use of double insulated tails on a ladder?


Sorry for my ignorance

Kind Regards
Parents
  • I already changed the cables from the DNO ACB from double insulated tails to singles XLPE/AWA armoured on the ladder I mentioned

    Looks like all opinions converge to this
Reply
  • I already changed the cables from the DNO ACB from double insulated tails to singles XLPE/AWA armoured on the ladder I mentioned

    Looks like all opinions converge to this