This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Separate main bonding to outbuilding

Former Community Member
Former Community Member
Hi, I just wanted people’s thoughts on this please.

I have been to a job with a TN-S supply. A sub main feeds a separate building with an SWA, the armour being used as the CPC. I have calculated the armour has not the additional cross sectional area to used as the required main bonding. I understand from GN8 that the main bonding needs to be extended to the building as specified in size by BS7671. I realise that this main bond will run from the MET to the Earth marshalling terminal in the second building. My question is this:

The SWA is buried and cannot be dug up (well easily). There is a second duct that runs between the buildings which is empty, but it follows a different route to the SWA. I seem to remember reading that it is best to run a separate bonding cable in close proximity to the existing SWA, am I correct or did I dream this? Is it advisable not to run the additional cable via a different route? If so, my only option will be to TT the second building.


Thanks in advance.



KS
Parents
  • What do you mean by 'main bonding'?

    Only the largest of SWA cables need an additional core for cpc purposes.

    Are there extraneous pipes/structure that needs bonding in the 2nd building?

Reply
  • What do you mean by 'main bonding'?

    Only the largest of SWA cables need an additional core for cpc purposes.

    Are there extraneous pipes/structure that needs bonding in the 2nd building?

Children
No Data