Separate main bonding to outbuilding

Former Community Member
Former Community Member
Hi, I just wanted people’s thoughts on this please.

I have been to a job with a TN-S supply. A sub main feeds a separate building with an SWA, the armour being used as the CPC. I have calculated the armour has not the additional cross sectional area to used as the required main bonding. I understand from GN8 that the main bonding needs to be extended to the building as specified in size by BS7671. I realise that this main bond will run from the MET to the Earth marshalling terminal in the second building. My question is this:

The SWA is buried and cannot be dug up (well easily). There is a second duct that runs between the buildings which is empty, but it follows a different route to the SWA. I seem to remember reading that it is best to run a separate bonding cable in close proximity to the existing SWA, am I correct or did I dream this? Is it advisable not to run the additional cable via a different route? If so, my only option will be to TT the second building.


Thanks in advance.



KS
Parents
  • Former Community Member
    0 Former Community Member
     You may like to refer to table 54.8, in all cases the SWA armour is large enough for main bonding up to 95mm2. Remember the main bonding conductor(s) never need to be larger than the supply neutral even with PME, and for 100A supplies 10mm2 is normally considered adequate.


    But consider if the incoming supply neutral is say 120 mm2 and you're taking a 25 mm2 4c SWA out to a building that requires main bonding.....................


    Regards


    BOD
Reply
  • Former Community Member
    0 Former Community Member
     You may like to refer to table 54.8, in all cases the SWA armour is large enough for main bonding up to 95mm2. Remember the main bonding conductor(s) never need to be larger than the supply neutral even with PME, and for 100A supplies 10mm2 is normally considered adequate.


    But consider if the incoming supply neutral is say 120 mm2 and you're taking a 25 mm2 4c SWA out to a building that requires main bonding.....................


    Regards


    BOD