This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Earth Fault Loop Impedance with Safety Generator

Former Community Member
Former Community Member
Do I take this into consideration? If so how do I size wire in a building with a safety generator? What is my "Ze" when the supply switches from DNO to the safety generator? How do diesel generators behave during faults?


Parents
  • That will not occur because 32A (instant trip) is available. Faults that will not clear will be on main or submain circuits where the power available is not sufficient. Earth faults on final circuits are the same, the present protection will work.
Reply
  • That will not occur because 32A (instant trip) is available. Faults that will not clear will be on main or submain circuits where the power available is not sufficient. Earth faults on final circuits are the same, the present protection will work.
Children
No Data