This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Waveform/wavecon cable sizing

Just had a quote in from Western Power for a new 100a 3 phase supply. There is approximately 100m between the pole mounted transformer and the cut out and the DNO has specified 185mm wavecon cable.. this seems like an overkill to me, the pole transformer is 50Kva and it seems like 95mm would be more appropriate!  Not sure what voltage drop on waveform cable is like but compared with regular SWA 95mm still seems plenty big enough.. Thoughts on this would be appreciated! Thanks




Parents
  • I didn't actually make the application but I believe 69kva was asked for in line with wanting a 100a per phase supply. A fast EV charger was the only declared load.
Reply
  • I didn't actually make the application but I believe 69kva was asked for in line with wanting a 100a per phase supply. A fast EV charger was the only declared load.
Children
No Data