Logic problem in OSG - trivial

Page 79 OSG (blue edition)


Lcn is max fault current .......although the breaker may no longer be usable.

Lcs is max fault current .......can interupt safely without loss of performance.


.........


For domestic installations, the PFC is unlikely to exceed 6kA , up to which value the Lcn will equal Lcs.


usable , maybe usable, certainly usable?


Parents
  • There is no faulty logic in the OSG or indeed BS 60898.


    When Ics = Icn, it means that there is no range where an MCB would safely break a current but not remain serviceable.


    It's all about design.


    If the PSSC is 5 kA, you may select a 6 kA MCB.


    If it is 7 kA, you may select a 10 kA MCB because Ics = 7.5 kA.


    If it is 8 kA, you need at least a 16 kA MCB because where Icn is > 10 kA, Ics = 0.5 x Icn. I suspect that when you get into this territory, there will be something before the MCB.
Reply