S.W.A. Armour Earthing.

Which regulations(s) require the steel wire armouring of a S.W.A. cable to be earthed if it is NOT used as a circuit protective conductor?


Case 1. Cable buried underground.


Case 2. Cable NOT buried underground.


Z.
Parents
  • The armour is cable containment, so as such it is an exposed conductive part, and must be Earthed to cause automatic disconnection of the supply.. 411.3.2


    I assume you are trying to have some kind of competition or was this a genuine inquiry. I refer you to the index of BS7671, exposed conductive part.
Reply
  • The armour is cable containment, so as such it is an exposed conductive part, and must be Earthed to cause automatic disconnection of the supply.. 411.3.2


    I assume you are trying to have some kind of competition or was this a genuine inquiry. I refer you to the index of BS7671, exposed conductive part.