Which regulations(s) require the steel wire armouring of a S.W.A. cable to be earthed if it is NOT used as a circuit protective conductor?
Case 1. Cable buried underground.
Case 2. Cable NOT buried underground.
Z.
In this case, an undetected fault to armour might leave the armour "live" and wouldn't necessarily be detected by the tests prescribed in BS 7671 (insulation resistance test to cpc or earth won't pick it up) - you'd specifically need to test to armour. What if the outer sheath becomes damaged at some point?
In this case, an undetected fault to armour might leave the armour "live" and wouldn't necessarily be detected by the tests prescribed in BS 7671 (insulation resistance test to cpc or earth won't pick it up) - you'd specifically need to test to armour. What if the outer sheath becomes damaged at some point?