lyledunn:
Maybe that’s the point Z is making, is the wire armour an exposed conductive part. Maybe not according to the definition.
I have an old copy of Guidance Note 8 2004. It says that even when the armouring is not in service as a protective conductor it still has to be earthed as it is an exposed-conductive-part.
But is it?
Case 2.
If the glands are shrouded the brass glands can't be touched. The armour can't be touched as it is covered in insulation. And if glanded into an insulating plastic enclosure all is safe init? Is the armour really
an exposed-conductive-part?
Z.
davezawadi (David Stone):
The armour is cable containment, so as such it is an exposed conductive part, and must be Earthed to cause automatic disconnection of the supply.. 411.3.2
I assume you are trying to have some kind of competition or was this a genuine inquiry. I refer you to the index of BS7671, exposed conductive part.
Suspicious David. No competition here, just a serious enquiry.
Z.