Does plastic conduit provide insulation ... or is it there for mechanical protection?
Does the sheath of a cable provide insulation ... or is it there for mechanical protection?
The situation still remains that, if you don't insulate the armour in the enclosure, it's not "finger-proof" from the perspective of accidental contact by a skilled or instructed person on opening the enclosure.
AJJewsbury:Two simultaneously-accessible "earth" potentials. "just not exposed to touch when the box is shut."
Inside an enclosure is perfectly OK for bare hazardous live conductors - are you really suggesting we need to go further for differing Earthed conductors?
I think that I can see both sides of the argument here. To my mind, 411.3.1.1 does not apply because the simultaneously accessible conductive parts are not exposed. That is until the lid of the enclosure is removed, but applying it in those circumstances seems absurd.
In an enclosure, there might be line conductors 400 V apart, but an electrician would approach them with care. The problem with the now exposed CPCs is that it isn't necessarily obvious that they may be at different potentials. Clear labelling must be the solution, otherwise the enclosure would have to be 7 feet long!
gkenyon:
Does plastic conduit provide insulation ... or is it there for mechanical protection?
Does the sheath of a cable provide insulation ... or is it there for mechanical protection?
Cable sheath and plastic conduit> Electrical insulation and/or mechanical protection? That is the question.
It is primarily for mechanical protection BUT also by virtue of its construction and material offers electrical insulation as well.
Z.