11 KV cables.

Until fairly recently, underground 11 KV cables were invariably 3 core, paper insulated, lead covered, with an earthed steel wire armouring. Then came the more modern plastic insulated cables, with earthed armour and a red plastic over sheath to distinguish them from LV cables.


However the modern trend seems to be a bundle a 3 single core cables, each with an aluminium core, plastic insulation, copper wire armouring and a red plastic sheath.

Why is this used ? It seems to me that 3 single core cables would be more costly to manufacture, and more labour intensive to joint or terminate, than one 3 core cable.

I fail to see the advantage, but presume that there must be some advantage, or why make the change ?
Parents
  • Johno12345:

    the bundled cable enters through the same gland, so I assume its a new type of gland to accommodate the three separate cables

    The gland plates will be non ferrous to avoid the heating effect of circulating eddy currents or perhaps slots between the holes, preferably if indoor transformers. If the plates are painted, use a magnet to test if unsure.


    Jaymack
Reply
  • Johno12345:

    the bundled cable enters through the same gland, so I assume its a new type of gland to accommodate the three separate cables

    The gland plates will be non ferrous to avoid the heating effect of circulating eddy currents or perhaps slots between the holes, preferably if indoor transformers. If the plates are painted, use a magnet to test if unsure.


    Jaymack