broadgage:
DNOs tend where possible to run 11Kv cables in a ring formation, in order that any substation on that ring may receive power from either direction.
Contrary to domestic ring final circuits, DNO practice is often to run with the ring "open" at one point, this point being selected so as to minimise losses. If a fault occurs, then the faulty section of the ring can be isolated by operation of the "ring main switches" in the substations, and supply restored before repairs are completed.
Hmm I had assumed that in normal operation the ring was closed and only opened at two isolators if one (or more than one adjacent) point at the substation required isolation..
broadgage:
DNOs tend where possible to run 11Kv cables in a ring formation, in order that any substation on that ring may receive power from either direction.
Contrary to domestic ring final circuits, DNO practice is often to run with the ring "open" at one point, this point being selected so as to minimise losses. If a fault occurs, then the faulty section of the ring can be isolated by operation of the "ring main switches" in the substations, and supply restored before repairs are completed.