Any idea how this translates into a disconnection time?
As a first bash realise that the disconnections times quoted for 230V TN systems assume a touch voltage of 110-130V, and for TT systems a shock voltage equal to the full mains voltage is assumed. And if you then look at the figures for say 400V and higher then that is comparable to a system at half the voltage in a 'wet' condition.
Any idea how this translates into a disconnection time?
As a first bash realise that the disconnections times quoted for 230V TN systems assume a touch voltage of 110-130V, and for TT systems a shock voltage equal to the full mains voltage is assumed. And if you then look at the figures for say 400V and higher then that is comparable to a system at half the voltage in a 'wet' condition.