davezawadi (David Stone):
There is no problem having a TNC-S supply and an Earth rod, this is "protective multiple Earthing" in reality. If the Earth wiring in the property is not continuous, this is a problem as it is not permitted to have multiple Earthing systems in one installation. The alleged TT part will be very obvious by the provision of RCD protection at the DB, but a simple continuity test will immediately tell you what is happening. If two Earthing systems I would code C2 as it could be dangerous.
Many old Norfolk installations were originally TT earthed. I have come across old earth rods buried under new extension foundations. The house has then been converted to P.M.E. but the rod left in by the builders.
Most modern P.M.E. installations have a notice informing us of such by the main cut out.
I have recently seen an old installation converted to P.M.E. but have left in two original earth electrodes as there is no harm in doing so, but every benefit in leaving them. The big house used to be two homes but is now just one after conversion.
Main bonding will cover any differences in potential of conducting pipes etc. within an installation if required.
Z.
davezawadi (David Stone):
There is no problem having a TNC-S supply and an Earth rod, this is "protective multiple Earthing" in reality. If the Earth wiring in the property is not continuous, this is a problem as it is not permitted to have multiple Earthing systems in one installation. The alleged TT part will be very obvious by the provision of RCD protection at the DB, but a simple continuity test will immediately tell you what is happening. If two Earthing systems I would code C2 as it could be dangerous.
Many old Norfolk installations were originally TT earthed. I have come across old earth rods buried under new extension foundations. The house has then been converted to P.M.E. but the rod left in by the builders.
Most modern P.M.E. installations have a notice informing us of such by the main cut out.
I have recently seen an old installation converted to P.M.E. but have left in two original earth electrodes as there is no harm in doing so, but every benefit in leaving them. The big house used to be two homes but is now just one after conversion.
Main bonding will cover any differences in potential of conducting pipes etc. within an installation if required.