I just winder if there is too much paranoia surrounding the loss of a neutral in a PME system in a built-up area. Maybe different out in the sticks, but with local substations being relatively plentiful in urban areas what is really the risk?You could well be right. Lower risk than we perceive perhaps. I was going through a concerned phase at the time. The 14th edition used to require that single phase sockets on different phases be kept at least 2m apart. Was there really a risk if single phase appliances were supplied by sockets on different phases? What were the real life reported accidents?
Z.
Back in the days of unearthed lighting circuits I suspect that the risks were significant.
An unearthed brass light switch or pendant lamp holder was fairly low low risk in an office or factory with wooden floors.
However two such switches or lamp holders and connected to different phases (or poles of a DC supply) and within reach would be dangerous.
Hence the old regulation of one pole or phase per room, with an exception for large rooms where this was impractical, in which case different phases or poles of a DC supply were permitted if 6 feet, later 2 meters apart.
The general use of plastic lamp holders and light switches and the earthing of lighting circuits rendered the regulation pointless, and it was removed, correctly in my view.
Zoomup:whjohnson:
I just winder if there is too much paranoia surrounding the loss of a neutral in a PME system in a built-up area. Maybe different out in the sticks, but with local substations being relatively plentiful in urban areas what is really the risk?You could well be right. Lower risk than we perceive perhaps. I was going through a concerned phase at the time. The 14th edition used to require that single phase sockets on different phases be kept at least 2m apart. Was there really a risk if single phase appliances were supplied by sockets on different phases? What were the real life reported accidents?
Z.
Back in the days of unearthed lighting circuits I suspect that the risks were significant.
An unearthed brass light switch or pendant lamp holder was fairly low low risk in an office or factory with wooden floors.
However two such switches or lamp holders and connected to different phases (or poles of a DC supply) and within reach would be dangerous.
Hence the old regulation of one pole or phase per room, with an exception for large rooms where this was impractical, in which case different phases or poles of a DC supply were permitted if 6 feet, later 2 meters apart.
The general use of plastic lamp holders and light switches and the earthing of lighting circuits rendered the regulation pointless, and it was removed, correctly in my view.