This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Type B RCDs

Increasingly, I am seeing a requirement for Type B RCDs in industrial applications, particularly where servo drives are used.


The preference is Type B RCBOs however, these are quite rare and not all manufacturers make them.


Aside from the high cost and short supply due to demand from EV and PV applications, how do others address this situation?


If the earthing is adequate, cables to the motors are run in trays and there is additional bonding to the motor housing, is there really a need for an RCD?
Parents
  • The manufacturer of the servo drives recommend a Type B RCD

    Still probably worth clarifying whether the manufacturer means:

    a) Should always be supplied via a B-type RCD, or

    b) Where RCD protection is required, it should be B-type.


    So if b) that might be to your advantage in you have a TN system.


       - Andy.
Reply
  • The manufacturer of the servo drives recommend a Type B RCD

    Still probably worth clarifying whether the manufacturer means:

    a) Should always be supplied via a B-type RCD, or

    b) Where RCD protection is required, it should be B-type.


    So if b) that might be to your advantage in you have a TN system.


       - Andy.
Children
No Data