Control Panel in an Acidic Environment

We are looking at installing a 316L Control panel within an environment where Sulfuric Acid is handled extensively.


Where can I look to understand what special requirements are needed for this environment?

I understand that Hydrogen Sulphide turns Copper into Copper Sulphate - which has a significantly lower conductivity level;

To mitigate/slow down that reaction, tinning exposed copper is usually practiced - but I don't know what is required for Tri-rated cabling and components such as Contactors etc.


The control panel is only going to be open for maintenance purposes, so the internals aren't going to be subjected to much vapour, and any spills would be on the outside of the panel.

I have a feeling that as the components are protected by the panel, to IP54 minimum, that the corrosion would be at a slow enough rate to reasonably not have to worry about it when thinking about the life expectancy of the panel - but any advise and references would be appreciated.


Thanks
Parents
  • Very useful, thanks. I hadn't considered plastic, as I thought it would melt where as Stainless Steel would show to be more resistant; guess it depends on the plastic!


    The customer has 316L Stainless Steel everywhere, and the employees aren't wearing breathing apparatus; just appropriate gloves.

    My impression is that it isn't an inherently dangerous place to be, like ATEX; I was just worried about the panel being in that environment 24/7 for years.


    In regards to tri-rated cabling, are there any special precautions I should be taking? I've asked our supplier about "tinned" tri-rated and they only do it by the kilometer; but I don't know if I need it or if I'm being overly cautious.
Reply
  • Very useful, thanks. I hadn't considered plastic, as I thought it would melt where as Stainless Steel would show to be more resistant; guess it depends on the plastic!


    The customer has 316L Stainless Steel everywhere, and the employees aren't wearing breathing apparatus; just appropriate gloves.

    My impression is that it isn't an inherently dangerous place to be, like ATEX; I was just worried about the panel being in that environment 24/7 for years.


    In regards to tri-rated cabling, are there any special precautions I should be taking? I've asked our supplier about "tinned" tri-rated and they only do it by the kilometer; but I don't know if I need it or if I'm being overly cautious.