Hi All,


Has anyone any experience calculating time delay maximum earth electrode resistance for time delayed RCDs, im looking at Table 3A in Appendix 3 but cant quite my head around it.


Standard 500ma would get 100ohms Ra. 


(50v / 500ma) x 1000 = 100RA

4557a7ce2499a05c386ab10a81e7c400-huge-image.png

The manufactuer used has setting for the 500ma time delay for 0.15s, 0.25s, 0.5s, 1s, 2.5s and 5s. I cant quite work out how that relates to the attached table.


Are the 0.15s and 0.25s faster than non delay? Id assume not, as its a delay


Some worked examples for the 500ma would be very helpful, im trying to discriminate with a downstream 300ma standard RCCB.


Thanks!
Parents
  • Although, the 300ma rcd is not 3x more than the upfront 500ma rcd. What are your thoughts on this?

    There's a small risk of lack of discrimination there - since RCDs usually can trip anywhere between >0.5x and ≤1x their rating, so the 500mA unit (if enthusiastic) could trip with residual currents above 250mA where the 300mA unit (if lazy) might not trip until 300mA - so if you had a residual current in the 250-300mA range (say due to moisture getting in somewhere or cumulative protective conductor currents if you have multiple downstream RCDs) there's a possibility of the 500mA unit tripping rather than the 300mA one.


       - Andy.
Reply
  • Although, the 300ma rcd is not 3x more than the upfront 500ma rcd. What are your thoughts on this?

    There's a small risk of lack of discrimination there - since RCDs usually can trip anywhere between >0.5x and ≤1x their rating, so the 500mA unit (if enthusiastic) could trip with residual currents above 250mA where the 300mA unit (if lazy) might not trip until 300mA - so if you had a residual current in the 250-300mA range (say due to moisture getting in somewhere or cumulative protective conductor currents if you have multiple downstream RCDs) there's a possibility of the 500mA unit tripping rather than the 300mA one.


       - Andy.