Wagos in a 2G socket backbox....

Former Community Member
Former Community Member
I'm running through the options with regards to terminating a 4mm2 ring when it comes to the sockets. For some of the 2G sockets there is plenty of space to easily / reliably terminate the 4mm2 cable, in others not so much.


What would be a whole lot easier (there is plenty of space as I fitted 35mm back boxes) would be to loop in and out via a couple of wago 221 3-way connectors using the 3rd way as a spur to the socket, allowing just a single cable needing to be clamped down at the socket terminal itself.


I'm sure I won't have been the first to have thought of this.


Thoughts please? The only limitation I can see is that I would'nt be able to spur off the socket (but could of course just use a wago with more ways).


It has been a long week and I just wanted to sense check this........


Thanks in advance


James
Parents
  • Installation method may preclude 2.5 (e.g. methods 101# or 103) as the current carrying capacity has to be at least 20 A.


    Volt drop is another potential reason - assuming 30 mA RCD protection is provided at the DB or CU as ring is feeding socket-outlets - ring length end-to-end exceeds 106 m {see Table 7.1(i) of OSG}


    Or perhaps it was simply in a specification for some reason ...
Reply
  • Installation method may preclude 2.5 (e.g. methods 101# or 103) as the current carrying capacity has to be at least 20 A.


    Volt drop is another potential reason - assuming 30 mA RCD protection is provided at the DB or CU as ring is feeding socket-outlets - ring length end-to-end exceeds 106 m {see Table 7.1(i) of OSG}


    Or perhaps it was simply in a specification for some reason ...