Sparkingchip:
Really you are looking at getting (2 x4.0) + 2.5 into the terminals to allow for a spur, which should be perfectly achievable because you could be using the same fittings for a 4.0 mm radial circuit.
You should not be having a problem in the first place.
Andy Betteridge.
Agreed ... BUT you may be surprised that spurring off a 4 mm2 ring or radial exceeds the terminal capacity stated in BS 1363-2:
11.5 Line and neutral terminals in fixed socket‑outlets shall permit the connection, without special preparation, of one, two or three 2.5 mm2 solid or stranded or of one or two 4 mm2 stranded conductors as given in Table 4 of BS 6004:2012.
and
11.6 Earthing terminals in fixed socket‑outlets shall permit the connection, without special preparation, of one, two or three 1.5 mm2 or 2.5 mm2 solid or stranded or of one or two 4 mm2 stranded conductors.
This terminal capacity is what's quoted in a number of manufacturer's ranges ... so the OP really does have a point, especially if you want to spur off anywhere it's a good idea, and perfectly reasonable in my opinion.
Sparkingchip:
Really you are looking at getting (2 x4.0) + 2.5 into the terminals to allow for a spur, which should be perfectly achievable because you could be using the same fittings for a 4.0 mm radial circuit.
You should not be having a problem in the first place.
Andy Betteridge.
Agreed ... BUT you may be surprised that spurring off a 4 mm2 ring or radial exceeds the terminal capacity stated in BS 1363-2:
11.5 Line and neutral terminals in fixed socket‑outlets shall permit the connection, without special preparation, of one, two or three 2.5 mm2 solid or stranded or of one or two 4 mm2 stranded conductors as given in Table 4 of BS 6004:2012.
and
11.6 Earthing terminals in fixed socket‑outlets shall permit the connection, without special preparation, of one, two or three 1.5 mm2 or 2.5 mm2 solid or stranded or of one or two 4 mm2 stranded conductors.
This terminal capacity is what's quoted in a number of manufacturer's ranges ... so the OP really does have a point, especially if you want to spur off anywhere it's a good idea, and perfectly reasonable in my opinion.