This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Wagos in a 2G socket backbox....

Former Community Member
Former Community Member
I'm running through the options with regards to terminating a 4mm2 ring when it comes to the sockets. For some of the 2G sockets there is plenty of space to easily / reliably terminate the 4mm2 cable, in others not so much.


What would be a whole lot easier (there is plenty of space as I fitted 35mm back boxes) would be to loop in and out via a couple of wago 221 3-way connectors using the 3rd way as a spur to the socket, allowing just a single cable needing to be clamped down at the socket terminal itself.


I'm sure I won't have been the first to have thought of this.


Thoughts please? The only limitation I can see is that I would'nt be able to spur off the socket (but could of course just use a wago with more ways).


It has been a long week and I just wanted to sense check this........


Thanks in advance


James
Parents
  • Which is probably one of the reasons that some electricians have said over the years that a radial should not have spurs.


    So working to product standards you should able to get the two 4.0 mm in, but maybe not a 2.5 mm spur.


    If you are using Wago connectors you do need the bigger size of three way for line and neutral, so it gets a bit crowded in the back box with the big red Wagos in there. There’s an overlap on sizes for 2.5 mm so you can use either size for it.
Reply
  • Which is probably one of the reasons that some electricians have said over the years that a radial should not have spurs.


    So working to product standards you should able to get the two 4.0 mm in, but maybe not a 2.5 mm spur.


    If you are using Wago connectors you do need the bigger size of three way for line and neutral, so it gets a bit crowded in the back box with the big red Wagos in there. There’s an overlap on sizes for 2.5 mm so you can use either size for it.
Children
No Data