mapj1:
..had a call from a man ..his socket didn't work! It didn't, as the carer had plugged an extension lead in to run a heater ..
His father had bought the house in 1934 and had electricity put in and a socket.
Assuming it was not a 13A plug being forced into a round pin socket - just about possible with some designs- my money is on the socket being on a 5A fused radial, and therefore not man enough for the heater.
Mike.
It was a 13A socket as someone in the distance past had changed the 15A to 13A but naturally left the lead cable in.
Lighting was lead and the whole place had just a 15a MEM switchfuse for the socket and a couple of 'porcelain ceiling roses' with 5a fusewire into lead 1.044 twin cable for lighting.
mapj1:
..had a call from a man ..his socket didn't work! It didn't, as the carer had plugged an extension lead in to run a heater ..
His father had bought the house in 1934 and had electricity put in and a socket.
Assuming it was not a 13A plug being forced into a round pin socket - just about possible with some designs- my money is on the socket being on a 5A fused radial, and therefore not man enough for the heater.
Mike.
It was a 13A socket as someone in the distance past had changed the 15A to 13A but naturally left the lead cable in.
Lighting was lead and the whole place had just a 15a MEM switchfuse for the socket and a couple of 'porcelain ceiling roses' with 5a fusewire into lead 1.044 twin cable for lighting.