Sparkingchip:Chris Pearson:
If the cable is surface mounted, AND a core is being used as the CPC, AND the cable is neatly terminated into enclosures with insulating glands, then I agree that there are no ECPs, so the armour does not have to be earthed.
So you completely disagree with the extract from the IET Guidance Note 8 which I posted?
Yes, because exposed-conductive-part = conductive part of equipment which can be touched ... .
I cannot think of any circumstances when you would specify SWA, but not use it as intended, but that wasn't the issue in the OP.
Sparkingchip:Chris Pearson:
If the cable is surface mounted, AND a core is being used as the CPC, AND the cable is neatly terminated into enclosures with insulating glands, then I agree that there are no ECPs, so the armour does not have to be earthed.
So you completely disagree with the extract from the IET Guidance Note 8 which I posted?
Yes, because exposed-conductive-part = conductive part of equipment which can be touched ... .
I cannot think of any circumstances when you would specify SWA, but not use it as intended, but that wasn't the issue in the OP.