Just trying to find a regulation that states a reason why the armoured metal of surface-mounted SWA needs earthing. Obviously, when buried underground, it does - 522.8.10.  I have read previous posts on this, but the question seems to have remained unanswered.

It would be considered best practice to at least earth the supply end, but best practice is not regulation. And, considering the statement at the end of Chapter 12, could it not be argued that short runs of surface-mounted armoured without earthing are ‘safe’? Where is the risk?

The armour does not meet the definition of an exposed conductive part when neatly terminated so it can not be touched – under what fault conditions could it become live?

SWA conductors are not double insulated, but is the risk any less than conductors in a plastic conduit?

Manufacturer instructions… it could be that they stipulate that the armour needs to be earthed, but where these are not available for review, how can a non-conformity be raised?

I’d appreciate any replies that point to a specific regulation or group of regulations.

Thanks in advance.

Parents
  • The law in England is permissive, that is to say that you can do whatever you will unless it is forbidden.


    If you can demonstrate that not earthing the armour of SWA as we have discussed is forbidden, so be it. Otherwise, leave well alone.
Reply
  • The law in England is permissive, that is to say that you can do whatever you will unless it is forbidden.


    If you can demonstrate that not earthing the armour of SWA as we have discussed is forbidden, so be it. Otherwise, leave well alone.